I am confused with an issue I recently saw on a project. My question is in regards to a fire pump controller for a 200HP 460V pump motor fed from two sources, one is a utility source and the other is a standby generator source. The controller has an integral ATS, but I did not have the specifications for it. The utility source was tapped from a 2500kVA xfmr secondary with no overcurrent protection, which I agree with according to 695.6.D. However, the breaker in the generator paralleling switchgear that is the second source to the controller is has a 300AT rating. I thought 695.4.B.1 stated that overcurrent protection should allow for carrying locked rotor current indefinitely. But then I see in 695.4.B the statement "Overcurrent protective devices between an on-site standby generator and a fire pump controller shall be selected and sized in accordance to 430.62 to provide short circuit protection only." My question is, why wouldn't the breaker feeding the controller from the generator be required to carry the LR current? What if the pump has a LR when the generator is supplying power?