Inspected a 20HP 208v 3 phase fire pump install
All aspects appear to meet NEC other than the LISTED controller has a main breaker marked "100 amps"
The motor has a LRA of 314 amps.
This would appear to be a problem but the controller is listed for the 20HP fire pump.
Is it possible on a Fire Pump Controller that the "100 amp" breaker is designed to handle the LRA ??