Hi all.
I am planning on making some additions to a sprinkler system in an existing building with a fire pump. The pump is 30hp, 240V 3ph and is wired to a 240V 3ph source.
Nameplate FLC on the pump motor is 40A which jives with T430-250.
I asked for recent pump test results from the Owner. One year ago churn amps were about 38A, 100% flow amps about 55A and 150% flow amps about 75A.
The most recent test from Aug. 2009, showed churn amps at 102A, 100% flow 120A and 150% flow at 135A.
The testing company apparently said nothing to the Owner in the way of raising any red flags.
Any idea what might be going on here? Design flows (500gpm at 100% and 750gpm at 150%) were not quite reached but close.
Thanks.
I am planning on making some additions to a sprinkler system in an existing building with a fire pump. The pump is 30hp, 240V 3ph and is wired to a 240V 3ph source.
Nameplate FLC on the pump motor is 40A which jives with T430-250.
I asked for recent pump test results from the Owner. One year ago churn amps were about 38A, 100% flow amps about 55A and 150% flow amps about 75A.
The most recent test from Aug. 2009, showed churn amps at 102A, 100% flow 120A and 150% flow at 135A.
The testing company apparently said nothing to the Owner in the way of raising any red flags.
Any idea what might be going on here? Design flows (500gpm at 100% and 750gpm at 150%) were not quite reached but close.
Thanks.