The NEC requires a direct connection to to the listed fire pump device from either a tap ahead of a service disconnect of separate service entrance however article 695.4(B) seems to give the impression that you can add a superviced disconnect device with over-current device between the source and the listed fire pump device.
Does 695.4(B) apply only in a feeder source situation per 695.3(B)(3)? It is a little confusing the way 695.4(B) is worded. I think the only situation where a disconnect and over current is allowed between a listed fire pump device and the source is in a situation that fall under a campus environment per Art 695.4(B). Is this correct? I see many violations of this rule if I am correct?
Does 695.4(B) apply only in a feeder source situation per 695.3(B)(3)? It is a little confusing the way 695.4(B) is worded. I think the only situation where a disconnect and over current is allowed between a listed fire pump device and the source is in a situation that fall under a campus environment per Art 695.4(B). Is this correct? I see many violations of this rule if I am correct?