Hey Gang,
Here's another point of confusion for me :ashamed1::
I attached a link to the NYC amendments for the 2008 NEC (hopefully you can just click on the link):
www.nyc.gov/html/dob/downloads/bldgs_code/electrical_code_local_law_39of2011.pdf
If you scroll down to page 72 (article 695 for fire pumps), under 695.4(A) Exception 2, it says if you have a limited service fire pump connected to both utility and an emergency generator, your disconnecting means does not need to be a service disconnecting means (so you can use a breaker on a panel to feed the limited service fire pump).
If you scroll down to page 73, under 695.4(B)(3) Exception, it says that your disconnecting means for fire pumps AND limited service fire pumps connected to emergency generators does not need to be service equipment (so I'm assuming you can again use a breaker on a panel to feed the pumps). Do they mean to say fire pumps and limited service fire pumps that are ONLY connected to emergency generators with no connection to a utility service? why wouldn't they mention 'utility service' the way they did above on page 72? If they also meant utility service (together with the emergency generator), why wouldn't the Fire Pump have been mentioned in Exception 2 on page 72 (as I wrote above for Limited Service Fire Pumps)?
Thanks! (hope that wasn't too confusing)
Here's another point of confusion for me :ashamed1::
I attached a link to the NYC amendments for the 2008 NEC (hopefully you can just click on the link):
www.nyc.gov/html/dob/downloads/bldgs_code/electrical_code_local_law_39of2011.pdf
If you scroll down to page 72 (article 695 for fire pumps), under 695.4(A) Exception 2, it says if you have a limited service fire pump connected to both utility and an emergency generator, your disconnecting means does not need to be a service disconnecting means (so you can use a breaker on a panel to feed the limited service fire pump).
If you scroll down to page 73, under 695.4(B)(3) Exception, it says that your disconnecting means for fire pumps AND limited service fire pumps connected to emergency generators does not need to be service equipment (so I'm assuming you can again use a breaker on a panel to feed the pumps). Do they mean to say fire pumps and limited service fire pumps that are ONLY connected to emergency generators with no connection to a utility service? why wouldn't they mention 'utility service' the way they did above on page 72? If they also meant utility service (together with the emergency generator), why wouldn't the Fire Pump have been mentioned in Exception 2 on page 72 (as I wrote above for Limited Service Fire Pumps)?
Thanks! (hope that wasn't too confusing)