Fire pump disconnect.
A disconnect is being installedbetween the fire pump controller and the power source (a utility transformer)as allowed by NEC 695.4(B)(1). The codereads “A single disconnecting means and associated overcurrent protectivedevices shall be permitted…” Does this requirement mean that a disconnect aheadof the controller must have overcurrent protection? If overcurrent protectionis not required, is 125% the size of the full load current the size for thedisconnect rating and not locked rotor current like it would be for overcurrentprotection?
A disconnect is being installedbetween the fire pump controller and the power source (a utility transformer)as allowed by NEC 695.4(B)(1). The codereads “A single disconnecting means and associated overcurrent protectivedevices shall be permitted…” Does this requirement mean that a disconnect aheadof the controller must have overcurrent protection? If overcurrent protectionis not required, is 125% the size of the full load current the size for thedisconnect rating and not locked rotor current like it would be for overcurrentprotection?