Sparky2791
Senior Member
- Location
- Northeast, PA
- Occupation
- Electrical Design
I am sure this has been asked before but....
First question
If one of my power supplies for a fire pump is a tap ahead of the main service disconnect with the service feed still over to the fire pump, following all the rules for that, outside underground or overhead if the rooms are next to each other.
Per 230.70 I require a service disconnecting means on the feed (service).
Can the circuit breaker in the fire pump transfer switch/controller be the service disconnect assuming it is rated as service entrance equipment?
If not;
Does the service disconnect require overcurrent protection? If it does not, can the disconnect itself be rated for locked rotor current? So lets say the FP motor FLA is 156A LRC is 907A without OCP in the switch a 200A switch would be sufficient but with OCP I would need a 1000A switch.
Second question
Second source of power is an emergency generator.
The gen set will have the main disconnect which protects the gen set. Than it will have a circuit breaker solely for the fire pump and one for life safety loads. Does the circuit breaker protecting the gen set itself need to comply with 695.4(B) (2) (2) (b)?
Third Question
695.4(B) (3) applies to all disconnect unique to the fire pump.
Item (1)
Not sure the the breaker on the gen set would not be listed as suitable for use as service equipment (?) Not wired as a separately derived system in my case - Solid Neutral transfer switch
Item (2) the breaker can be lockable so looks like no issue here
Item (3)
Would the breaker installed directly on the generator be in violation of this item. Technically not in the same enclosure, panelboard, switchboard, switchgear or MCC?
Item (4) no problem to comply
Let me know if there are any questions.
Thanks for looking.
First question
If one of my power supplies for a fire pump is a tap ahead of the main service disconnect with the service feed still over to the fire pump, following all the rules for that, outside underground or overhead if the rooms are next to each other.
Per 230.70 I require a service disconnecting means on the feed (service).
Can the circuit breaker in the fire pump transfer switch/controller be the service disconnect assuming it is rated as service entrance equipment?
If not;
Does the service disconnect require overcurrent protection? If it does not, can the disconnect itself be rated for locked rotor current? So lets say the FP motor FLA is 156A LRC is 907A without OCP in the switch a 200A switch would be sufficient but with OCP I would need a 1000A switch.
Second question
Second source of power is an emergency generator.
The gen set will have the main disconnect which protects the gen set. Than it will have a circuit breaker solely for the fire pump and one for life safety loads. Does the circuit breaker protecting the gen set itself need to comply with 695.4(B) (2) (2) (b)?
Third Question
695.4(B) (3) applies to all disconnect unique to the fire pump.
Item (1)
Not sure the the breaker on the gen set would not be listed as suitable for use as service equipment (?) Not wired as a separately derived system in my case - Solid Neutral transfer switch
Item (2) the breaker can be lockable so looks like no issue here
Item (3)
Would the breaker installed directly on the generator be in violation of this item. Technically not in the same enclosure, panelboard, switchboard, switchgear or MCC?
Item (4) no problem to comply
Let me know if there are any questions.
Thanks for looking.