Good morning and go easy on me... new to "complex" Fire Pump installations! Need some "grounded/ing" help. Essentially the system is setup as follows:
Here though, the separate 1000A OCP / panel is the "service disconnect". Neutral / Ground bonding occurs there. NOW downstream we now have an equipment grounding conductor sized per 250.122... which intuitively doesn't make sense to me because of the function of that breaker... but that's how I am reading the code.
What was running as #4 into the service now becomes a 2/0 from the service to the ATS... basically the size of the conductors we are running for the pump (3/0 for a 156 FLA before 125% added)!
Is this a equipment ground sized per 250.122 or a SSBJ sized per 250.102?
Thanks for any headache you can stave off!
- A 480V Service Transformer has the secondary lugs hits two separate service rated switchboards.
- One Switchboard is building loads.
- We can ignore this service for the rest of the question.
- The other service switchboard is the fire pump service disconnect. It houses a 1000A main breaker for short circuit protection and sized to carry locked rotor for a 125 HP motor (again, 480V, 908A per 430.251).
- We bring a supply side bonding jumper to this OCP device / panel. The neutral ground bond occurs here as well, and we run an Electrode Grounding Conductor to ground from here.
- One Switchboard is building loads.
- However... that fire pump service panel does not house the ATS or the Controller!
- From the fire pump service disconnect mentioned above we run to a separate ATS.
- From the separate ATS... we run to a separate fire pump controller.
- From the separate fire pump controller, we finally hit the 125 HP fire pump.
Here though, the separate 1000A OCP / panel is the "service disconnect". Neutral / Ground bonding occurs there. NOW downstream we now have an equipment grounding conductor sized per 250.122... which intuitively doesn't make sense to me because of the function of that breaker... but that's how I am reading the code.
What was running as #4 into the service now becomes a 2/0 from the service to the ATS... basically the size of the conductors we are running for the pump (3/0 for a 156 FLA before 125% added)!
Is this a equipment ground sized per 250.122 or a SSBJ sized per 250.102?
Thanks for any headache you can stave off!