I have a client that is at a refinery that wants to feed their electric fire pump from one of their substations. From what I can tell in NEC 695.3(C), I need to make sure:
1. The sources in 695.3(A) are not practicable [according to the AHJ and/or the insurance carrier I assume].
2. A refinery is considered as a multi-building campus-style complex (it seems to be as described in the Handbook, "This distribution arrangement is common in industrial and institutional campus settings"). Again, according to the AHJ/insurance carrier, I assume.
3. There will be a dedicated backup generator as an alternate source and the OCPD's will be selectively coordinated per (C)(2) and (C)(3).
Does this sound doable? All other questions regarding fire pumps that I can find discuss getting power from the utility.
Thanks,
Norm