I have fire pump, jockey pump fed from customer owned 13.8kV to 480/277V three phase delta to wye transformer. The setting is multibuilding campus-style complex and in accordance with NEC 2017 Article 695.3(C)(2). The customer owned 13.8kVA to 480/277V also feed another switchboard downstream as well as the fire pump and jockey pump. See attached below.
NEC 2017 Article 695.5(C) allows this. However I am confused with NEC 2017 Article 695.5(C)(2) where it says the following “..overcurrent protection is provided for the transformer in accordance with 450.3 and for the feeder in accordance with 215.3 and such that the overcurrent protection device(s) is selected or set to carry indefinitely the sum of locked rotor current of the fire pump motor(s), the pressure maintenance pump motor(s), the full load current of the associated fire pump accessory equipment and 100 percent of the remaining loads supplied by the transformer. The requirement to carry the locked rotor currents indefinitely shall not apply to conductors or devices other than overcurrent devices in the fire pump motor circuit(s).”
It is very confusing what exactly is feeder in this case such as transformer secondary conductor
For feeder protection does the NEC 2017 require transformer secondary overcurrent protection for secondary side conductor feeding the fire pump sized per locked rotor current or not?
NEC 2017 Article 695.5(C) allows this. However I am confused with NEC 2017 Article 695.5(C)(2) where it says the following “..overcurrent protection is provided for the transformer in accordance with 450.3 and for the feeder in accordance with 215.3 and such that the overcurrent protection device(s) is selected or set to carry indefinitely the sum of locked rotor current of the fire pump motor(s), the pressure maintenance pump motor(s), the full load current of the associated fire pump accessory equipment and 100 percent of the remaining loads supplied by the transformer. The requirement to carry the locked rotor currents indefinitely shall not apply to conductors or devices other than overcurrent devices in the fire pump motor circuit(s).”
It is very confusing what exactly is feeder in this case such as transformer secondary conductor
For feeder protection does the NEC 2017 require transformer secondary overcurrent protection for secondary side conductor feeding the fire pump sized per locked rotor current or not?