Re: Fire Pump Fed From Utility & Generator
Sorry to take so long to get back with you folks. I had a doctor's appointment, and then an appointment to carry my daughter deer hunting.
Let me see if I can try to paint you a better picture of what I'm trying to do. The fire pump service is 3 phase with a grounded conductor for the return of fault current to the utility source. The grounded conductor is bonded to the transfer switch frame in the normal source position. I am planning to use a separate service for the fire pump fed off the utility transformer, just as SCEPE suggested.
The generator is set up as separately derived system. Neutral will be grounded to the generator frame and the GEC at that point. It will feed a distribution panel, that in turn will feed emergency, legally required stand-by, and possibly optional loads as well through transfer switchs. The fire pump transfer switch is fed from this panel for it's stand-by source, and an EGC is carried with the phase conductors for return of fault current to the generator.
The problem appears when the transfer switch is in the Normal (Utility source)position and I put a line to ground fault elsewhere on the system. Fault current flows across this EGC between the generator distribution panel & fire pump transfer switch and gets back into the grounded conductor by the bond to the frame of the transfer switch, instead of completely flowing to the main panel as it should.
In looking at this, I have just had a thought. Would it be permissable instead of making a hard connection with the EGC from the Generator distribution panel to the frame of the fire pump transfer switch, to tie this conductor to the Generator source side of the fourth pole? The frame of the transfer switch will continue to be bonded to the common pole as I have tried to describe above I realize the conduit needs to be non-conductive.
For you folks out there. I'm using the IEEE Orange book diagrams for a separately derive source, a main service, and a 4 pole transfer switch. What I have added is the fire pump transfer switch and a generator distribution panel. I do have a sketch but don't have a clue as to how to post it on this site. Would be happy to fax to someone for a look.
For SCEPE, When it rains it pours, But I have already seen worse, and every dog (oops, I mean rooster) has its day. I just hope to live long enough to see it again! Go Cocks!