Hello,
Can you please tell me if the Tap rule: "The ampacity of the Tap conductor is not less than one third of the rating of the overcurrent device protecting the feeder conductors" [240.21(B)(2) and (4)] applies to the conductors feeding the overcurrent device? Please see the single line below for reference. My confusion is if those conductors are considered "Service conductors" or "Feeder conductors", I have understood that, that tap rule doesn't applies to Service conductors. Where in the NEC or NFPA can I find something in specific to this matter?.
Thank you.

Can you please tell me if the Tap rule: "The ampacity of the Tap conductor is not less than one third of the rating of the overcurrent device protecting the feeder conductors" [240.21(B)(2) and (4)] applies to the conductors feeding the overcurrent device? Please see the single line below for reference. My confusion is if those conductors are considered "Service conductors" or "Feeder conductors", I have understood that, that tap rule doesn't applies to Service conductors. Where in the NEC or NFPA can I find something in specific to this matter?.