We currently are working on a fire pump/generator install for a high rise building in NJ (22 stories). There is an existing fire pump being fed from a switch in the main switch gear which is being direct replaced. The new fire pump was designed to be tapped ahead of the main switch and CT's via Coated MC and routed to the new Fire Pump CT Cabinet/disconnect on the other side of the electric room. After the CT/Disconnect the MC Cable switches over to Vitalink Cable routed through the non fire rated common space areas. The town approved the design, however up PSE&G's inspection for the shut down they are requesting the Coated MC to be change to RGS. The engineer seems to believe that if we tap on the other side of the CT's, still ahead of the main switch that this will remove the requirement for RGS from PSEG. This has gone pretty far down the rabbit hole over the last month while the engineer tries to come up with a solution to avoid a measly $5K change order to satisfy the utility requirement. Internally, we believe the correct thing to do is satisfy the utility requirement. Is the engineer correct that by tapping on the outgoing side of the CT's and sharing the existing metering should eliminate the RGS requirement and allow the Coated MC to remain? Any insight is appreciated.