To a 100HP fire pump, is an MI feeder emergency feeder (i.e. run from the generator) comprised of 3#1 &1#6.
Per 310.15(B)17 in the 75 deg column, #1's and #6's are rated for 195A and 95A respectively.
They could have gone with just a 3 phase feeder but they didn't. They included the neutral.
My question is that given this feeder does not exceed 200A, by code allowance, would it be permissible to run a neutral that is 50% that of the phase conductors.
Wouldn't the feeder need to be over 200A, per 220.61 to reduce the size of the neutral at all?
By the way, the OCPD is a fused switch with 175A fuses (assuming they are dual element type). A bit low but OK I guess assuming the pump has a soft start or drive.
In any event, what do you think?
Thanks,
Mike
Per 310.15(B)17 in the 75 deg column, #1's and #6's are rated for 195A and 95A respectively.
They could have gone with just a 3 phase feeder but they didn't. They included the neutral.
My question is that given this feeder does not exceed 200A, by code allowance, would it be permissible to run a neutral that is 50% that of the phase conductors.
Wouldn't the feeder need to be over 200A, per 220.61 to reduce the size of the neutral at all?
By the way, the OCPD is a fused switch with 175A fuses (assuming they are dual element type). A bit low but OK I guess assuming the pump has a soft start or drive.
In any event, what do you think?
Thanks,
Mike