Fire Pump Feeder

Status
Not open for further replies.

jbt260

Member
Location
Ohio
Occupation
Electrical Engineer
Does the feeder from the main service breaker to the fire pump controller have to be encased in concrete or have a 2-hr rating if the breaker and controller are in the same room?
 

texie

Senior Member
Location
Fort Collins, Colorado
Occupation
Electrician, Contractor, Inspector
If you have a feeder to a FP controller the feeder will have to be 2 hour rated. If these are service conductors they have to be outside the building per the NEC definition. Concrete encasement is one option to get them outside the building. Just a fire rating alone would not be allowed if service conductors.
You say "feeder from main service breaker". A fire pump cannot be supplied from the load side of the building service. In most applications you would have a connection ahead of the service equipment and run service conductors outside the building directly to the fire pump controller in the fire pump room.
Maybe you could clarify your situation.
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
Does this answer your question ?
From 695.6
Exception to (A)(2)(d): The supply conductors located in the electrical equipment room where they originate and in the re pump room shall not be required to have the minimum 2-hour re separation or reresistance rating, unless otherwise required by 700.10(D) of this Code.
 

gadfly56

Senior Member
Location
New Jersey
Occupation
Professional Engineer, Fire & Life Safety
Does this answer your question ?
From 695.6
Exception to (A)(2)(d): The supply conductors located in the electrical equipment room where they originate and in the re pump room shall not be required to have the minimum 2-hour re separation or reresistance rating, unless otherwise required by 700.10(D) of this Code.
^^^^That right there.
 