^^^^That right there.Does this answer your question ?
From 695.6
Exception to (A)(2)(d): The supply conductors located in the electrical equipment room where they originate and in the re pump room shall not be required to have the minimum 2-hour re separation or reresistance rating, unless otherwise required by 700.10(D) of this Code.