Fire Pump Feeder
Kjc59
Audubon, NJ
Best way to feed a fire pump assuming a separate section isn’t included in the gear and the utility transformer can’t handle any more conduits. Man-hole with splice connectors? The service is 4,000A and I need to feed a 75 HP fire pump obviously ahead of the service disconnect
This is a 4000A service which means that it likely has a CT Cabinet in the building (assuming its not metered at the transformer).
Assuming the utility Co approved, why not turn the existing CT Cabinet into a large wireway and splice the existing service feeder to feed the Fire Pump service, and then re-feed a new CT Cabinet for the existing 4000A service?
Nothing is installed. But the gear is ordered with out a fire pump section. Is it feasible to hit a manhole after the transformer and splice in there and send one feed to the FP and then one to the metered/CT gear section
It's feasible but this is entirely up to the power company. I had a project one time for an existing building where the existing service conductors between the Utility XFRMR and meter center were damaged by a saw blade, so we had to put in a hand hole to pull out the damaged conductors and we had to get special permission in writing from the power company to tap the existing service conductors.
Personally, I think the bigger issue could actually be voltage drop. Fire Pump feeders are required have a voltage drop of less than 15% under Locked Rotor Amp (LRA) Conditions. Assuming 208/3, the LRA of the 75HP fire pump would be about 1200 Amps, and then you have to add the demand amps of the non-fire pump loads to that.
What is the calculated demand of the "normal" loads on this service, and how far are you running?
FYI: If this is new construction then its probably a new transformer. The power co should be a able to put an additional cabinet next to the transformer to land additional conductors. The easiest thing may be to just email the power company.
Yeah I guess on smaller services you could do a hand hole with an 8 or 12 port splice connectors but once you SE conductors start reaching 6+ sets you need to land on something with lugs, which assuming has to be done above grade and not ingrade.
Can you revise the gear order? I would just add a cable tap section between the CT's and the main. There might already be a shipping split there.
Does the gear have a utility pull section for the utility conductors?
If so Tap it from there an set another meter and disconnect in the electric room.
You'd just have to talk to the ahj about the service conductors to the pump or go underground with them
A lot of poco’s have tap boxes remotely from the transformer with buss bars and a larger footprint for more conduits. Since it’s a new install, the project engineer or customer should have already talked to the poco engineers.