mshields
Senior Member
- Location
- Boston, MA
When distributing power in a hospital from a standby generator that serves Life Safety, Critical and Standby loads, I keep the Emergency breakers in one vertical section (so Life Safety and Critical) and I put the standby loads in a second barriered switchboard section. (if a smaller application I come off a wire way with separate devices). The point is per 700.10 these need to be separated. We cannot, as was once common, use a distribution panelboard for these breakers. Where I have a fire pump, that cannot even be in the same switchboard. And so for that I have breaker in it's own section. I believe this is correct as I've been doing it for years. But I'm looking for the requirement in the NEC that requires this added level of separation that is required for Fire Pumps and I'm having a hard time finding it.
Can anyone help?
Can anyone help?