steve holt
Member
- Location
- Hawaii
I have a fire pump being fed by a normal (reliable source) and a backup from an emergency generator. The normal is being fed by a breaker (sized for locked rotor) in a separate section of the main switch gear and is routed directly to the fire pump controller/ATS. The emergency feeder is being fed through a series of breakers starting with the breaker on the generator, which is then routed to a distribution board, which is then routed to another distribution boards and finally to the fire pump controller/ATS. According to my AHJ, the breaker feeding the fire pump has to be isolated from breakers feeding other loads. In the past 26 years I have had some projects where the secondary feeder (emergency) is fed from a separate breaker on the generator, but most are fed through a series of breakers which are not in a separate enclosure. I have read through section 695 over and over but can't get a firm grip as to what the code is saying.
1. Does the breaker on the secondary feeder (emergency) need to be isolated from other loads?
2. If it does, does this only apply to the final breaker, or all breakers along the way?
1. Does the breaker on the secondary feeder (emergency) need to be isolated from other loads?
2. If it does, does this only apply to the final breaker, or all breakers along the way?