Fire Pump Fuse Type

Status
Not open for further replies.

msteiner

Senior Member
Location
Maryland
I have a fused disconnect as my service disconnect feeding a fire pump. In order to comply with the NEC requirement to NOT provide overload protection in the overcurrent device feeding the FP, should I be providing a non-time delay fuse (i.e. instantaneous only protection)?
 

msteiner

Senior Member
Location
Maryland
695.5(B) says secondary overcurrent protection shall not be permitted, I interpret that as no fusible disconnect

695.5(B) refers to transformer secondary, and applies when you have a transformer downstream of the utility service entrance. My fused disconnect is serving as the utility service disconnect.
 

alive wire

Member
Location
Phoenix, AZ US
I definitely don't know everything which is why I hang out on this forum, but if the goal of running a fire pump is to keep it going to catastrophic failure

Sent from my SM-N900V using Tapatalk
 

msteiner

Senior Member
Location
Maryland
I guess my question really has to do with fuse trip characteristics. If I were using a circuit breaker I would call for a motor circuit protector type, with magnetic-only protection, and no overload protection. I don't know what fuse type is analogous to an MCP breaker.
 

mayanees

Senior Member
Location
Westminster, MD
Occupation
Electrical Engineer and Master Electrician
'sup Matt

'sup Matt

NFPA 20, section 9.2 "Normal Power" requires disconnect and overcurrent protection to occur in the listed fire pump controller, so I don't think a disconnect ahead of the controller is allowed.
Fusing in the controller is sized to allow locked rotor current indefinitely, and the type would be driven by the mounting arrangement in the controller and the required ampacity and voltage.
 

msteiner

Senior Member
Location
Maryland
Hey J!

Hey J!

What I've left out of the issue is that I'm using a transformer to step up the voltage from 208V to 480V, so my fused disconnect is ahead of the transformer. Because of this, I believe a fused disconnect is required.
 

gadfly56

Senior Member
Location
New Jersey
Occupation
Professional Engineer, Fire & Life Safety
What I've left out of the issue is that I'm using a transformer to step up the voltage from 208V to 480V, so my fused disconnect is ahead of the transformer. Because of this, I believe a fused disconnect is required.

If you use a fused disconnect, it should be sized for the locked rotor current. Same with anything that might be further upstream.
 

Tony S

Senior Member
For security of supply to fire pumps this is one of the best setups I’ve come across. The two red switches are direct off the transformer incoming. Even if the main LV breaker trips the pump supply is assured (Incoming isolated in this picture). The board had two incomers and therefore four pumps in total.

The supply to the fire pump panels was MI.

6_zpslhtve2ug.jpg
 