Hi,
Just wondering what will be the size of ground wire from the Fire pump controller to the Fire pump for a 575/3/60 250HP pump (FLA 242A).
According to Table 250.122 it is sized according to the OCPD, which in this case is 600% X FLA of the fire pump.
it seems quite high to use 3/0-4/0 ground wire for a 242A feed.
Am I on the right track?
Just wondering what will be the size of ground wire from the Fire pump controller to the Fire pump for a 575/3/60 250HP pump (FLA 242A).
According to Table 250.122 it is sized according to the OCPD, which in this case is 600% X FLA of the fire pump.
it seems quite high to use 3/0-4/0 ground wire for a 242A feed.
Am I on the right track?