Grouch
Senior Member
- Location
- New York, NY
Hi all,
For a high rise building, i have a fire pump on the rooftop (say the 20th floor). It's connected to a transfer switch. The normal feed to the transfer switch comes from the basement, via a fused service disconnect switch (sized at 600% of the pump FLA) tapped off the main switchboard. And the emergency feed to the transfer switch comes from a breaker (sized at 150% of the pump FLA) in the generator.
Here are my 2 questions:
1) What size ground wire do i use in the feeder that runs from the load side terminal of the transfer switch to the fire pump? I would imagine it's sized based on the fuses inside the service disconnect switch, rather than the breaker from the generator, since during either normal or emergency operation, the largest sized OCPD is in the service disc. switch (600% versus 150%).
2) What size ground wire do i use in the feeder from the switchboard tap to the service disc. switch? These are tap conductors, so how do i size the ground wire if there's ground bus bars inside the switchboard?
Thanks!
For a high rise building, i have a fire pump on the rooftop (say the 20th floor). It's connected to a transfer switch. The normal feed to the transfer switch comes from the basement, via a fused service disconnect switch (sized at 600% of the pump FLA) tapped off the main switchboard. And the emergency feed to the transfer switch comes from a breaker (sized at 150% of the pump FLA) in the generator.
Here are my 2 questions:
1) What size ground wire do i use in the feeder that runs from the load side terminal of the transfer switch to the fire pump? I would imagine it's sized based on the fuses inside the service disconnect switch, rather than the breaker from the generator, since during either normal or emergency operation, the largest sized OCPD is in the service disc. switch (600% versus 150%).
2) What size ground wire do i use in the feeder from the switchboard tap to the service disc. switch? These are tap conductors, so how do i size the ground wire if there's ground bus bars inside the switchboard?
Thanks!