Our office needing to design a fire pump installation for an existing building. The fire pump & its jockey pump will be feed in accordance with 695.3(A)(1) as a seperate electric utility service. The feeder will be run from the utility transformer, underground exterior to the building, stubbed into the pump room and connected to the pump controllers. The conductors are sized based on 430.6(A)(1) and Table 430.150. Voltage drop has been verfied as to be less than 15% as called for in 695.7.
My question is regarding the grounding of the new service. Article 695 makes no mention of grounding therefore am I to treat this as a seperate service and size the ground according to Table 250.66 and run that to the water pipe and a supplemental ground such as a ground rod? Which table would be used for the ground wire from the controller to the pump?
I find it very odd that the issue of Grounding is not at least mentioned and some direction is given back to Article 250.
Thanks for your help.
My question is regarding the grounding of the new service. Article 695 makes no mention of grounding therefore am I to treat this as a seperate service and size the ground according to Table 250.66 and run that to the water pipe and a supplemental ground such as a ground rod? Which table would be used for the ground wire from the controller to the pump?
I find it very odd that the issue of Grounding is not at least mentioned and some direction is given back to Article 250.
Thanks for your help.