Hello everyone.
I am designing a new fire pump with a new 208-3 phase service to be put in a existing warehouse. I only have done one fire pump because typically, achieving the required flow without one isn't an issue.
The new fire pump will be 75 HP with a 1-1/2 HP jockey pump.
I pretty much have this thing wrapped up, however I have a big question.
According to the table in the NEC for a 208-3 phase load (75HP) the FLC is 211amps, however the LRA is 1200A!!! For some reason im reminded of a code that says the fused disconnect (one only) the fuses must be sized for LRA, however everything else can be sized for FLC. including the wire size.
AN overview of the installation
Right now, I have a new service going to the exterior (3) #600s +Ground, then it goes to a 1200A fused disconnect, from there it goes over head to the fire pump controller (the run is with RHW wire by the way).
There is no way I could size the service for 1200A. The fire pump controller that is specifically made for the 75HP pump will only accept up to a certain wire size, it certainly wont accept a 1200A feeder.
Any help with this would be greatly appreciated.
I am designing a new fire pump with a new 208-3 phase service to be put in a existing warehouse. I only have done one fire pump because typically, achieving the required flow without one isn't an issue.
The new fire pump will be 75 HP with a 1-1/2 HP jockey pump.
I pretty much have this thing wrapped up, however I have a big question.
According to the table in the NEC for a 208-3 phase load (75HP) the FLC is 211amps, however the LRA is 1200A!!! For some reason im reminded of a code that says the fused disconnect (one only) the fuses must be sized for LRA, however everything else can be sized for FLC. including the wire size.
AN overview of the installation
Right now, I have a new service going to the exterior (3) #600s +Ground, then it goes to a 1200A fused disconnect, from there it goes over head to the fire pump controller (the run is with RHW wire by the way).
There is no way I could size the service for 1200A. The fire pump controller that is specifically made for the 75HP pump will only accept up to a certain wire size, it certainly wont accept a 1200A feeder.
Any help with this would be greatly appreciated.