Hello Everyone:
I’m working on a project where a fire pump upgrade is required. The current fire pump will be replaced with like capacity. However, after further investigation I found the following:
1. This is a high rise building where the building house a MV 13.8KV utility switchgear. The building is served from three-MV 13.8KV feeders from different substation (2-preferd & Reserve).
2. There are multiple double ended unit substations serving the building. The unit substations steps down the 13.8KV to 480V.
3. The existing fire pump is currently fed from a switchboard that is fed from the unit substation via 800A fuse. No other source is feeding the pump. The feeder to the pump is served from overhead conduits.
My conclusions are:
1. The fire pump doesn’t comply with the NEC code requirement due to the fire pump needs to be powered from two different sources; one normal source and a generator or two normal sources (since the two service feeders are coming from two different substation). Is this correct?
2. Does the feeder to the fire pump coming from the switchboard as described above a code compliance or it has to come directly from the unit substation?
3. The current fire pump is 75HP but the fuse size used in the switchboard to feed 800A, I believe it should 600% of the motor FLA, correct?
4. The current feeders to the fire pump are ran overheads with conduits and wires, I believe this needs to be fire resistant assembly such as MI cable, correct?
5. I’m thinking to bring this to code by powering the new pump with two feeders from two alternate normal sources but will be from switchboards down stream of the unit substations since no spare fuses are available in unit substation (The use of generator as an alternate feed is a challenging due to the condition of the generators), change the feeders to MI cables if no other options are available. Do you see any issue with this approach?
6. Someone mention that I have to keep 10ft separation between the two fire pump feeders, not sure where this come, any idea?
Thanks,
I’m working on a project where a fire pump upgrade is required. The current fire pump will be replaced with like capacity. However, after further investigation I found the following:
1. This is a high rise building where the building house a MV 13.8KV utility switchgear. The building is served from three-MV 13.8KV feeders from different substation (2-preferd & Reserve).
2. There are multiple double ended unit substations serving the building. The unit substations steps down the 13.8KV to 480V.
3. The existing fire pump is currently fed from a switchboard that is fed from the unit substation via 800A fuse. No other source is feeding the pump. The feeder to the pump is served from overhead conduits.
My conclusions are:
1. The fire pump doesn’t comply with the NEC code requirement due to the fire pump needs to be powered from two different sources; one normal source and a generator or two normal sources (since the two service feeders are coming from two different substation). Is this correct?
2. Does the feeder to the fire pump coming from the switchboard as described above a code compliance or it has to come directly from the unit substation?
3. The current fire pump is 75HP but the fuse size used in the switchboard to feed 800A, I believe it should 600% of the motor FLA, correct?
4. The current feeders to the fire pump are ran overheads with conduits and wires, I believe this needs to be fire resistant assembly such as MI cable, correct?
5. I’m thinking to bring this to code by powering the new pump with two feeders from two alternate normal sources but will be from switchboards down stream of the unit substations since no spare fuses are available in unit substation (The use of generator as an alternate feed is a challenging due to the condition of the generators), change the feeders to MI cables if no other options are available. Do you see any issue with this approach?
6. Someone mention that I have to keep 10ft separation between the two fire pump feeders, not sure where this come, any idea?
Thanks,