malachi constant
- Minneapolis
Working on my first high rise, and it's the first time I've had to connect the fire pump to the generator. Sorry in advance for the muddied questions. My biggest one is about the jockey pump at the end of this post, but I'm not convinced all my assumptions up to that point are correct. All references are to NEC '08. I have a ~125HP fire pump and 1.5HP jockey pump.
State building code for high rises dictates the fire pump be fed from standby generator. I am having trouble navigating the codes but assume it is proper to put the fire pump on a transfer switch fed directly from utility and from generator breaker.
Per 695.4(A) the generator output breaker for the fire pump will be in a separate enclosure from other generator breakers. Knowing this isn't my area of expertise I've included verbiage in the generator and transfer switch specifications that the fire pump is on the gen set, and have asked the mechanical engineer to include a similar note in the fire pump specifications.
I'm assuming a 600A breaker, transfer switch and disconnect for the fire pump. How can I tie the jockey pump into the generator? Can I tap off the transfer switch or fire pump disconnect? If the FP is fed with two sets of 4/0 I can't parallel a #12 from the transfer switch to the JP, can I? Or is the JP normally fed from the FP controller (single point connection)?
Thanks in advance.
Thanks in advance.