I need some help with a fire pump question.
I have a 100 HP/480V, nameplate FLA 115A and code letter C on a fire pump motor. The CB, controller, and disconnect is sized and provided by the equipment provider. I calculated the LRC at 480A. A seperate service size installed is 480V/200A. In Article 625.4(B)(1) the OCPD shall be selected or set to carry the LRC of the motor. Will the 200A MCB fill this requirement? The inspector says I need to install a 500A service for this fire pump. What is the proper answer and what am I missing?
I have a 100 HP/480V, nameplate FLA 115A and code letter C on a fire pump motor. The CB, controller, and disconnect is sized and provided by the equipment provider. I calculated the LRC at 480A. A seperate service size installed is 480V/200A. In Article 625.4(B)(1) the OCPD shall be selected or set to carry the LRC of the motor. Will the 200A MCB fill this requirement? The inspector says I need to install a 500A service for this fire pump. What is the proper answer and what am I missing?