Pse&g asked my take on Fire Pump Metering. There is a push on rating metering at lock rotor current. One site has a 50 HP motor 208v ---430.250 says 143amps x 125% or 179amps.
A 200amp meter socket would be fine. But if we go by lock rotor current, a CT cabinet would need to be installed. 695.4 (2)a tells me only OCPD need to be rated @ lock rotor current and the 200a meter socket is ok.
Am I correct?
A 200amp meter socket would be fine. But if we go by lock rotor current, a CT cabinet would need to be installed. 695.4 (2)a tells me only OCPD need to be rated @ lock rotor current and the 200a meter socket is ok.
Am I correct?