The situation:
Fire Pump Design
480V-3PH-WYE service lateral to 4000Amp gear lineup
Incoming Utility section, then CT section, then fire pump tap section, then the service main
Fire pump is 100+HP and is 480V-3PH-delta
The inspector has required us to include a neutral conductor with the normal feeder to the fire pump ATS/Controller. The load is a totally balanced 3PH load. The ATS has a solid neutral and the EM generator is not bonded (not a separately derived system). He did not site a code section so I'm left to assume.
I assume he is requiring this because of 230.82(5), which requires the tap for a fire pump from the service supply to be treated as service entrance conductors, thus requiring the neutral. I have no intention of bonding this neutral at the ATS/Controller, but rather landing it on a lug and calling it a day. But in a couple of cases the inspector made the contractor bond the neutral and ground a second time at the ATS/Controller, and provide a ground to the building grounding electrode system.
I have reserves about designing the 3PH delta fire pump tap normal feeder with this neutral conductor re-bonded a second time for fear that it may cause a problem with an objectionable path for current, and it seems a waste of good money and copper. I most certaily have no intention of bonding it again, or providing a second ground. I have been designing this feeder with an EG in lieu of the neutral. They are basically the same thing in this situation as they are all bonded together at the service gear and are sized based on 250.122. I may have been wrong for years and am now second guessing myself.
If the feeder conductors were coming directly off of the utility transformer and not through the service gear I could see the need for the neutral as the system is a wye system and is not bonded at this point. Except of course the secondary XO.
My question:
Has anyone else been required to do this, and what problems if any might it cause? Also is there an issue with not running this neutral and using only the EG?
Fire Pump Design
480V-3PH-WYE service lateral to 4000Amp gear lineup
Incoming Utility section, then CT section, then fire pump tap section, then the service main
Fire pump is 100+HP and is 480V-3PH-delta
The inspector has required us to include a neutral conductor with the normal feeder to the fire pump ATS/Controller. The load is a totally balanced 3PH load. The ATS has a solid neutral and the EM generator is not bonded (not a separately derived system). He did not site a code section so I'm left to assume.
I assume he is requiring this because of 230.82(5), which requires the tap for a fire pump from the service supply to be treated as service entrance conductors, thus requiring the neutral. I have no intention of bonding this neutral at the ATS/Controller, but rather landing it on a lug and calling it a day. But in a couple of cases the inspector made the contractor bond the neutral and ground a second time at the ATS/Controller, and provide a ground to the building grounding electrode system.
I have reserves about designing the 3PH delta fire pump tap normal feeder with this neutral conductor re-bonded a second time for fear that it may cause a problem with an objectionable path for current, and it seems a waste of good money and copper. I most certaily have no intention of bonding it again, or providing a second ground. I have been designing this feeder with an EG in lieu of the neutral. They are basically the same thing in this situation as they are all bonded together at the service gear and are sized based on 250.122. I may have been wrong for years and am now second guessing myself.
If the feeder conductors were coming directly off of the utility transformer and not through the service gear I could see the need for the neutral as the system is a wye system and is not bonded at this point. Except of course the secondary XO.
My question:
Has anyone else been required to do this, and what problems if any might it cause? Also is there an issue with not running this neutral and using only the EG?