Fire Pump OCP
augie47
Tennessee
Is there a situation where the conductors from a generator can be installed to a fire pump controller without short circuit protection. 695.6 advised that the power circuits shall not have overload protection, but I see no rule that allows the generator supply to have no protection.
I think you want 695.4(B)......If you are in the 2005 NEC.
Chris...I dont have the 2008 NEC Handy....is your reference to 694(B)(1) a move.....anyway I believe 695.4(B) will answer his question.