I looked at a job the other day that was a new 100 kw generator, ATS and new 480v 3p panelboard for the generator loads.
They want to connect computer and HVAC loads to this generator.
I thought that it all was good until they said that they wanted the Fire Pump on the generator also.
Without the fire pump I would call this a Standby System and not a Legally Required Standby System.
This job is in MA where we amend the 05 NEC.
700.9(D)(1) would require a two hour fire rated room and wiring.
The existing fire pump is connected to the line side of the main in the switchgear. The fire pump feeder leaves the top of the switchgear and goes to the fire pump disconnect in the same room as the switchgear. The load from the disconnect leaves the disconnect then is run through the wall to the outside and runs along the building to the fire pump at the other end of the building.
They want to connect the fire pump to the generator load panel.
I think that they need to add a second main breaker to the generator or connect the fire pump to the line side of the generator main and a second transfer switch listed for fire pumps and rated for the locked rotor current of the fire pump. And the normal source needs to remain.
Does the fire pump disconnect and transfer switch need to be in a two hour rated room and wiring outside the room be 2 hr rated also?
I am going to talk to the local AHJ, but what do you think?
They want to connect computer and HVAC loads to this generator.
I thought that it all was good until they said that they wanted the Fire Pump on the generator also.
Without the fire pump I would call this a Standby System and not a Legally Required Standby System.
This job is in MA where we amend the 05 NEC.
700.9(D)(1) would require a two hour fire rated room and wiring.
The existing fire pump is connected to the line side of the main in the switchgear. The fire pump feeder leaves the top of the switchgear and goes to the fire pump disconnect in the same room as the switchgear. The load from the disconnect leaves the disconnect then is run through the wall to the outside and runs along the building to the fire pump at the other end of the building.
They want to connect the fire pump to the generator load panel.
I think that they need to add a second main breaker to the generator or connect the fire pump to the line side of the generator main and a second transfer switch listed for fire pumps and rated for the locked rotor current of the fire pump. And the normal source needs to remain.
Does the fire pump disconnect and transfer switch need to be in a two hour rated room and wiring outside the room be 2 hr rated also?
I am going to talk to the local AHJ, but what do you think?