NEC 230.90 Requires overload protection for "Each ungrounded service conductor".
Exception No 4 states that for fire pump supply conductors, this shall comply with 695.4 (B)(2)(a).
The problem I am running into, is that the breaker in a SUSE rated fire pump controller does not meet the requirements in NEC 695.4 (B)(2)(a). If that is the case, would I not need an overcurrent protection device ahead of every fire pump controller? If not, can someone point me to the code which states that this is not required or why my assumptions are incorrect? I have checked with multiple manufacturers and they all indicated that the breakers in their controllers DO NOT meet the requirements in NEC 695.4 (B)(2)(a).
Exception No 4 states that for fire pump supply conductors, this shall comply with 695.4 (B)(2)(a).
The problem I am running into, is that the breaker in a SUSE rated fire pump controller does not meet the requirements in NEC 695.4 (B)(2)(a). If that is the case, would I not need an overcurrent protection device ahead of every fire pump controller? If not, can someone point me to the code which states that this is not required or why my assumptions are incorrect? I have checked with multiple manufacturers and they all indicated that the breakers in their controllers DO NOT meet the requirements in NEC 695.4 (B)(2)(a).