Hi fellas, I am sizing the overcurrent protection for a fire pump as required by NEC 695.4(1). The code says that I I shall size the OCPD to the motor locked rotor ampacity (inrush) current. The motor is a rated 200HP, 1450 Amps (LRC),
480V, 3-phase.
On the other side this fire pump is connected to a control box, which manual reads that the fire pump will be started at 40% of the Pump's LRC (580 Amps). Question: Shall I size the OCPD based on 1450A, or at 580A?
Thanks in advance for any input.