I'm trying to make sure I understand Article 695.4 and 695.6. The way I understand it, the overcurrent protection is sized based on the locked-rotor current, however the feeder is only sized on 125% of the FLA. Hypotheticaly if you had a 40HP fire pump you could have #4 CU on a 300 amp breaker? My second question would be if this is served from the utility transformer how would you have to size the direct wire meter socket. 100 amps based on 125% of FLA or 300 amp based on LRC. This is not based on an actual situation, just trying to understand.