- Location
- Lockport, IL
- Occupation
- Semi-Retired Electrical Engineer
Backup generator feeds a switchboard with two breakers in separate vertical sections. OK so far. One of the breakers (rated 200 amps) feeds the emergency ATS, and there is a panel (call it panel “E”) downstream of this ATS. The fire pump controller, with its own transfer switch, gets its normal power from a tap ahead of the main. The backup source to the fire pump comes from panel E. I have two problems with this arrangement.
Comments are welcome. FYI, I am doing a Peer Review, and this is one of my concerns with the project.
- If the utility service is lost during a fire scenario, the fire pump will need the successful operation of two ATSs, in order for it to have power. I can’t think of a code that this violates, but I don’t like it.
- The fire pump (20 HP, 208/3, with a FLA of 59.4 amps) will be fed via the 200 amp breaker. That breaker can’t sustain 6 x FLA indefinitely, and it is not limited to short circuit protection only. I think this violates 695.6(B)(3). My question is whether that article comes into play for the backup power source. I can’t think of why it wouldn’t, but I thought I would ask.
Comments are welcome. FYI, I am doing a Peer Review, and this is one of my concerns with the project.