Am I reading correctly ?
I have a fire pump installed in a building on multi-building campus supplied from a single transformer from a campus owned looped 12kv system.
If I'm reading Art 695 correctly it appears that I am dealing with 695(C) as we are dealing with a mutli-building facility and feeders not services.
If am depending on two feeders they would have to be derived from separate services not from the one "looped" service.
Other than a totally separate service or an on-site standby generator is there another alternative to supply the fire pump.
 
where is this building located? does the city or state building code have additional requirements for the fire pumps?