Am I reading correctly ?
I have a fire pump installed in a building on multi-building campus supplied from a single transformer from a campus owned looped 12kv system.
If I'm reading Art 695 correctly it appears that I am dealing with 695(C) as we are dealing with a mutli-building facility and feeders not services.
If am depending on two feeders they would have to be derived from separate services not from the one "looped" service.
Other than a totally separate service or an on-site standby generator is there another alternative to supply the fire pump.