Fire pump controller/ats:
- Normal power circuit comes from a tap to poco transformer's secondary side without protection.
- Generator power circuit comes from a main emergency distribution panel (1st panel downstream of standby generator) and this circuit is protected by a breaker in panel.
- On normal power side (utility power), no breaker is needed, but per NEC, if a breaker is installed between xfmr and fire pump, the breaker needs to be sized to handle motor inrush current, i.e., CB size = 6 x fire pump motor's FLA.
- For generator power circuit, per NEC, the breaker to serve circuit to fire pump is not required to size to carry motor inrush current but = 2.5 X motor's FLA (article 430 for thermal magnetic breaker).