Fire pump protection

Status
Not open for further replies.

anbm

Senior Member
Location
TX
Occupation
Designer
Fire pump controller/ats:
  • Normal power circuit comes from a tap to poco transformer's secondary side without protection.
  • Generator power circuit comes from a main emergency distribution panel (1st panel downstream of standby generator) and this circuit is protected by a breaker in panel.
Question:
  • On normal power side (utility power), no breaker is needed, but per NEC, if a breaker is installed between xfmr and fire pump, the breaker needs to be sized to handle motor inrush current, i.e., CB size = 6 x fire pump motor's FLA.
  • For generator power circuit, per NEC, the breaker to serve circuit to fire pump is not required to size to carry motor inrush current but = 2.5 X motor's FLA (article 430 for thermal magnetic breaker).
Question: when fire pump is on generator power, fire pump's inrush current never occur???
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
The generator will not likely be able to start the fire pump without a large voltage sag that serves to act as a soft start and reduce the inrush.
 
Location
United kingdom
Occupation
Builder
Fire pump controller/ats:
  • Normal power circuit comes from a tap to poco transformer's secondary side without protection.
  • Generator power circuit comes from a main emergency distribution panel (1st panel downstream of standby generator) and this circuit is protected by a breaker in panel.
Question:
  • On normal power side (utility power), no breaker is needed, but per NEC, if a breaker is installed between xfmr and fire pump, the breaker needs to be sized to handle motor inrush current, i.e., CB size = 6 x fire pump motor's FLA.
  • For generator power circuit, per NEC, the breaker to serve circuit to fire pump is not required to size to carry motor inrush current but = 2.5 X motor's FLA (article 430 for thermal magnetic breaker).
Question: when fire pump is on generator power, fire pump's inrush current never occur??? https://aperfectshinedetailing.com/
Is a fire pump required to have a rated separation from other spaces in the building?
 

gadfly56

Senior Member
Location
New Jersey
Occupation
Professional Engineer, Fire & Life Safety
Fire pump controller/ats:
  • Normal power circuit comes from a tap to poco transformer's secondary side without protection.
  • Generator power circuit comes from a main emergency distribution panel (1st panel downstream of standby generator) and this circuit is protected by a breaker in panel.
Question:
  • On normal power side (utility power), no breaker is needed, but per NEC, if a breaker is installed between xfmr and fire pump, the breaker needs to be sized to handle motor inrush current, i.e., CB size = 6 x fire pump motor's FLA.
  • For generator power circuit, per NEC, the breaker to serve circuit to fire pump is not required to size to carry motor inrush current but = 2.5 X motor's FLA (article 430 for thermal magnetic breaker).
Question: when fire pump is on generator power, fire pump's inrush current never occur???
The OCPD is sized for the locked rotor current, not the inrush.
 

tom baker

First Chief Moderator & NEC Expert
Staff member
Location
Bremerton, Washington
Occupation
Master Electrician
Most of the rules in Art 695 are extracted from NFPA 20. Suggest you get a copy of what ever version of NFPA 20 you AHJ has adopted
 