JJWalecka
Senior Member
- Location
- New England
695.6 (E) Pump wiring from the controllers to the pump motors shall be in Rigid Metal Conduit, Intermediate metal conduit, Liquid tight flexible metal conduit, or liquid tight flexible nonmetallic conduit Type LFNC-B, listed type MC cable with an impervious covering or type MI cable.
Rigid penetrates the concrete slab. Installation of 90 degree liquid tight connector would be ascetically pleasing. Installing conductors into the ninety degree connector is a project in itself. Mogul LB is an alternative but costly.
Would a weather proof trough sized in accordance with 314.28 (A)(2) be a violation of 695.6 (E)?
Justin J. Walecka
Rigid penetrates the concrete slab. Installation of 90 degree liquid tight connector would be ascetically pleasing. Installing conductors into the ninety degree connector is a project in itself. Mogul LB is an alternative but costly.
Would a weather proof trough sized in accordance with 314.28 (A)(2) be a violation of 695.6 (E)?
Justin J. Walecka