Fire Pump refeed

Status
Not open for further replies.

mshields

Senior Member
Location
Boston, MA
Working on a hospital that has the following distribution:

13.8kV S&C existing switchgear to remain
Primary metered.
Primary switches feed each of two 2500kVA transformers which in turn feed two ends of a double ended 480V switchgear lineup.

Now - We're replacing that double ended lineup as well as the two transformers lets say in kind (although now they're smaller). At present the Fire Pump is fed from a breaker in the double ended line up. I cannot immitate that I realize, but my question is do I have to tap one of the main switches in the 13.8kV gear or can I tap ahead of the 480V switchgear main. If it matters, the 13.8kV lineup and transformers are outside, the 480V switchgear is indoors.

Thanks,

Mike
 

chris kennedy

Senior Member
Location
Miami Fla.
Occupation
60 yr old tool twisting electrician
13.8kV S&C existing switchgear to remain
Primary metered.
Primary switches feed each of two 2500kVA transformers which in turn feed two ends of a double ended 480V switchgear lineup.

The primary switches are the service disconnect means. Sounds like you need a new service ahead of that to me.
 