wireman1 Senior Member Jul 19, 2017 #1 can pvc pipe be used for the circuits that are involved in connections to the fire pump and the controls for the system if the pvc is protected from physical damage . does pvc have a fire rating ? cite any codes that may apply
can pvc pipe be used for the circuits that are involved in connections to the fire pump and the controls for the system if the pvc is protected from physical damage . does pvc have a fire rating ? cite any codes that may apply
D Danelectron Member Location Astoria, Oregon Jul 19, 2017 #2 It doesn't appear so according to 695.6. Specifically (D).
kwired Electron manager Location NE Nebraska Occupation EC Jul 19, 2017 #3 Danelectron said: It doesn't appear so according to 695.6. Specifically (D). Click to expand... I agree. If encased in 2 inches or more of concrete your AHJ possibly may still allow it though.
Danelectron said: It doesn't appear so according to 695.6. Specifically (D). Click to expand... I agree. If encased in 2 inches or more of concrete your AHJ possibly may still allow it though.