I am reviewing a fire pump service. The pump motor is 25 hp. 480V 3 phase.
I am trying to determine the proper size conductors from the service mast through to the motor.
When I look at 695.6(C)(2), and follow it to 430.22 which refers me to 430.6(A)(1) which refers me to Table 430.250.
There I find 34A to be the full load rating. That times 1.25% equals 42.5A.
Then I read 183A locked rotor in Table 430.251(B).
So if I understand this correctly, the service conductors could be rated at 100A minimum.
The main disconnect breaker must be rated at 200A minimum.
The branch circuit breaker must also be rated at 200A minimum.
The conductors going to the moter controller and motor could be rated at 50A.
Am I reading this correct??