I'm looking over NEC 695 and I'm still a bit fuzzy about the protection requirements for a fire pump. What I've got is a non-fused Square D general duty safety safety switch right next to the utility meter, which is about 25ft from the fire pump controller. (Also has gen-side feed, and everything seems to check out there)
This is actually a multi-part question, first concerning short-circuit: The switch by itself doesn't have any general withstand rating, correct? With protection it would be a minimum of 10kA, so does it even require OCPD?
For conductor sizing: The FLA is 155 amps, so what's the minimum amp capacity for the feeder cables?
Next, would be OCPD sizing: The LRA of the pump/jockey combined is about 950A, so would a 1000A fuse be practical? Lastly, the switch nameplate shows a rating of only 200A, would it also need to be replaced? Or is everything fine as-is?
Sorry for the loaded question, but it seems that all of it needs to check out, any help is appreciated!
This is actually a multi-part question, first concerning short-circuit: The switch by itself doesn't have any general withstand rating, correct? With protection it would be a minimum of 10kA, so does it even require OCPD?
For conductor sizing: The FLA is 155 amps, so what's the minimum amp capacity for the feeder cables?
Next, would be OCPD sizing: The LRA of the pump/jockey combined is about 950A, so would a 1000A fuse be practical? Lastly, the switch nameplate shows a rating of only 200A, would it also need to be replaced? Or is everything fine as-is?
Sorry for the loaded question, but it seems that all of it needs to check out, any help is appreciated!