Currently finishing up construction on a fire pump job where the pump is fed from a dedicated service. Conduits are routed outside per 695. The fire pump is located in an abandoned transformer vault in the basement. Conduits penetrate the exterior basement wall directly into be fire pump controller. All is good, or so I thought.
I show up on site today and the electrical contractor has decided to relocate the fire pump controller to a different wall and routed the service conductors in conduit approximately 5' over to the pump controller. I noted that these conduits will now need to be concrete encased.
His argument is that once the service conductors enter the pump room, they are allowed to be run up to the controller without the concrete encasement. And of course, he has installed an LB where the conduit enters the room which can't be covered in concrete anyway. He says that this is a dedicated fire pump room now and some portion of the conduit can be installed as it runs into the fire pump controller.
I still read the code to say that any portion of the service run within the building would require 2" concrete encasement. Am I missing something?
thanks.
I show up on site today and the electrical contractor has decided to relocate the fire pump controller to a different wall and routed the service conductors in conduit approximately 5' over to the pump controller. I noted that these conduits will now need to be concrete encased.
His argument is that once the service conductors enter the pump room, they are allowed to be run up to the controller without the concrete encasement. And of course, he has installed an LB where the conduit enters the room which can't be covered in concrete anyway. He says that this is a dedicated fire pump room now and some portion of the conduit can be installed as it runs into the fire pump controller.
I still read the code to say that any portion of the service run within the building would require 2" concrete encasement. Am I missing something?
thanks.