Fire Pump Service

Status
Not open for further replies.

mobo

Member
Location
MO USA
So typically, what kind of service is ran to a fire protection pump?

3 wire ungrounded delta?

3 wire corner grounded delta?

some kind of 4 wire service?

An explanation of why would be appreciated as well. Thanks.
 

mobo

Member
Location
MO USA
So the fire pump doesn't have to be on it's own dedicated service? separate from the main facility's service?
 

gadfly56

Senior Member
Location
New Jersey
Occupation
Professional Engineer, Fire & Life Safety
So the fire pump doesn't have to be on it's own dedicated service? separate from the main facility's service?

If there is a POCO transformer on the property feeding the customer's switchgear in an electrical room, the usual deal is to tap the service ahead of the switchgear to provide a separate set of service conductors for the fire pump. If they pull the meter or the switchgear goes down for any reason, the fire pump will still run.
 

mobo

Member
Location
MO USA
If there is a POCO transformer on the property feeding the customer's switchgear in an electrical room, the usual deal is to tap the service ahead of the switchgear to provide a separate set of service conductors for the fire pump. If they pull the meter or the switchgear goes down for any reason, the fire pump will still run.

Makes sense. Thanks for the reply!
 

packersparky

Senior Member
Location
Wisconsin
Occupation
Inspector
If there is a POCO transformer on the property feeding the customer's switchgear in an electrical room, the usual deal is to tap the service ahead of the switchgear to provide a separate set of service conductors for the fire pump. If they pull the meter or the switchgear goes down for any reason, the fire pump will still run.

Here the POCO would require the fire pump to be metered.
 

kec

Senior Member
Location
CT
Occupation
Electrical Contractor
If there is a POCO transformer on the property feeding the customer's switchgear in an electrical room, the usual deal is to tap the service ahead of the switchgear to provide a separate set of service conductors for the fire pump. If they pull the meter or the switchgear goes down for any reason, the fire pump will still run.

Here the POCO would require the fire pump to be metered.

This is also the requirement in the state of CT.
 