A lot of debate around here on this one..
I have a 15hp fire pump with an fla of 46.2 amps and lrc of 257 amps.
my wire size for the motor feeder is 46.2x1.25 or 57.75 amps.
if I use a disconnect or breaker on the service to feed the pump it has to be sized for locked rotor current. So a 400 amp meter section with a 300 amp breaker is in order. But if I tap the power source and install no breaker or disconnect am I still required to use a 400 amp meter section? Or can I use a 200 amp meter? I'll probably be using #6 conductors. Since they are the weakest link in the chain won't the meltdown long before the 200 amp meter?
695.3(a) says that a single source shall be capable of suppling locked rotor current indefinitely.
I have a 15hp fire pump with an fla of 46.2 amps and lrc of 257 amps.
my wire size for the motor feeder is 46.2x1.25 or 57.75 amps.
if I use a disconnect or breaker on the service to feed the pump it has to be sized for locked rotor current. So a 400 amp meter section with a 300 amp breaker is in order. But if I tap the power source and install no breaker or disconnect am I still required to use a 400 amp meter section? Or can I use a 200 amp meter? I'll probably be using #6 conductors. Since they are the weakest link in the chain won't the meltdown long before the 200 amp meter?
695.3(a) says that a single source shall be capable of suppling locked rotor current indefinitely.