I've never been able to figure this out exactly what they want here.
In my opinion, the installation still needs to meet the requirements of 230.70 A 1. You need a service disconnect "nearest the point of entrance of the service conductors".
You also need to meet 230.50 B 1, which doesn't list MI cable.
So unless your fire pump controller is right next to the SWBD, I'd say you need an additional fused disconnect or circuit breaker.
But then there is the section Kwired posted - 230.72(B). The disconnect for the fire pump has to be remote from the other disconnects. So how can it be both "remote", and "closest to the point of entrance"?
The only way I see to meet both requirements is to not install OCP at the switchboard, and then run under the building slab (so the conductors are outside the building), and stub up at the fire controller so the disconnect at the controller is still "closest to the point of entrance."