I am powering a fire pump from a 480:208 transformer, the pump is 208V, 3-phase, 88Amps. My plan is to use a 75kva (88x.208x1.73x1.25=39.6 kva,). The service OCPD on the primary of the transfomrer will 250A((88x.208x6)/.48)=228.8Amps). My question how do I size the primary conductors to the transformer, would it simply be 48Amps (39.6/.48/1.73) and use #8s?
Thanks,