I have a Part Winding (Star / Delta) fire pump.
The building is under the 1999 code, and the part winding motor is not shown in the Fire Pump section. (Article 695-6)The manufacturer shows in the UL listing, to size conductors for the motor connection using 58% of the Motor FLA. My inspector demands the conductors be sized for 125% of the Motor FLA which makes the conductors a 4/0. Six 4/0 violates the wire bending space and wire fill within the peckerhead of the motor.
what is the solution?
The building is under the 1999 code, and the part winding motor is not shown in the Fire Pump section. (Article 695-6)The manufacturer shows in the UL listing, to size conductors for the motor connection using 58% of the Motor FLA. My inspector demands the conductors be sized for 125% of the Motor FLA which makes the conductors a 4/0. Six 4/0 violates the wire bending space and wire fill within the peckerhead of the motor.