This is a new installation of a fire pump in an existing building. The building has an attached transformer vault accessible from the outside. The engineer's drawings show to tap the secondary of the transformer in the vault, no OCPD or disconnecting means, and run a 2" GRC conduit through the ceiling app. 100' to the fir pump controller. the engineer spec's to use a fire resistant cable to meet the listing requirements of Circuit Conductors. I see these as service conductors, requiring to meet 695.6(A), thar requires them to be outside of the building.
Anyone familliar with fire pumps that can offer some input? Thanks in advance.
P.S. We are under 2008 NEC