695.5 Transformers. Where the service or system voltage is
different from the utilization voltage of the fire pump motor,
transformer(s) protected by disconnecting means and overcurrent
protective devices shall be permitted to be installed
between the system supply and the fire pump controller in
accordance with 695.5(A) and (B), or with (C). Only transformers
covered in 695.5(C) shall be permitted to supply loads
not directly associated with the fire pump system.
(A) Size. Where a transformer supplies an electric motor
driven fire pump, it shall be rated at a minimum of 125 percent
of the sum of the fire pump motor(s) and pressure maintenance
pump(s) motor loads, and 100 percent of the associated
fire pump accessory equipment supplied by the transformer.