hhsting
Senior Member
- Location
- Glen bunie, md, us
- Occupation
- Junior plan reviewer
Please see attached sketch. New service conductors go underground into building CT cabinet with one utility meter. In the utility CT cabinet one conductor feeds building main service disco and second conductor go underground and feed fire pump controller in the building which feed fire pump.
I see that NEC 2014 section 695.3(A)(1) says fire pump can be supplied by separate service or from connection located ahead of the service disconnecting means but not in the same enclosure as the service disconnecting means. I am just not sure which one applies to the attached sketch or none of the two applies
Question:
1. Would the attached configuration be considered new electric utility service for fire pump or not as mention 695.3(A)(1) version NEC 2014?
2. Would the attached configuration be considered connected ahead of the main service disconnecting means or not as mentioned 695.3(A)(1) version 2014 NEC?
I see that NEC 2014 section 695.3(A)(1) says fire pump can be supplied by separate service or from connection located ahead of the service disconnecting means but not in the same enclosure as the service disconnecting means. I am just not sure which one applies to the attached sketch or none of the two applies
Question:
1. Would the attached configuration be considered new electric utility service for fire pump or not as mention 695.3(A)(1) version NEC 2014?
2. Would the attached configuration be considered connected ahead of the main service disconnecting means or not as mentioned 695.3(A)(1) version 2014 NEC?
Last edited: